Bullseye Posted September 9, 2014 Share Posted September 9, 2014 I am changing my trane thermostat for a c4 to be able to do some scheduling. I want to be sure i do the correct wiring.As per the picture of the current one,24rc red ---------RC G green --------GY1 yellow ------- Y124c blue ---------???W1 white --------- W1W2/O orange----- W2Where does the 24c blue goes???Do I still need the jumper???Thanks for the help!Ooooops. No pictures allowed?? Link to comment Share on other sites More sharing options...
mstafford388 Posted September 9, 2014 Share Posted September 9, 2014 the blue goes in the TS/C all the way on the right. you do need the jumper between the 2 red terminals. Link to comment Share on other sites More sharing options...
Bullseye Posted September 9, 2014 Author Share Posted September 9, 2014 Thanks. Btw, power stealing should be off ?Tomorrow will be installing it.Thanks again Link to comment Share on other sites More sharing options...
Cyknight Posted September 9, 2014 Share Posted September 9, 2014 YES power stealing should be off. It rarely works anyway, and using the Blue to TS/C (Commom or COM on your furnace) defeats the need to begin with. In fact leaving it on with a Com connection WILL give you grief. Link to comment Share on other sites More sharing options...
Bullseye Posted October 17, 2014 Author Share Posted October 17, 2014 Finally today were able to change the thermostat. Everything seem to be working fine!!!!Thanks all for your help! Link to comment Share on other sites More sharing options...
Bullseye Posted October 18, 2014 Author Share Posted October 18, 2014 Finally today were able to change the thermostat. Everything seem to be working fine!!!!Thanks all for your help!Talked too fast!!Back the old one until I have some time to try it again! Link to comment Share on other sites More sharing options...
Bullseye Posted March 29, 2015 Author Share Posted March 29, 2015 Today I am trying again with the thermostat.Took the trane out and put the c4 in.Wiring as previously indicated, the display indicates cooling but its blowing hot air. The switches on back of the unit are secondary- electric. / primary-electric and mode- conventionalWhat I am doing wrong?????Thanks for your help Link to comment Share on other sites More sharing options...
Matt Lowe Posted March 29, 2015 Share Posted March 29, 2015 what type of system do you have conventional heat pump gas or electric? Link to comment Share on other sites More sharing options...
Bullseye Posted March 29, 2015 Author Share Posted March 29, 2015 Its Electric, Link to comment Share on other sites More sharing options...
Matt Lowe Posted March 29, 2015 Share Posted March 29, 2015 looks like you have everything correct. I would confirm this color termination on the handler itself just to make sure they wired everything straight thru. a picture of this panel also would be helpful Link to comment Share on other sites More sharing options...
Bullseye Posted March 29, 2015 Author Share Posted March 29, 2015 I have to get in the attic to check it out. Looks I will install the old thermostat and after checking the handler, plus some pictures, will get into it again.Thanks for your help Link to comment Share on other sites More sharing options...
Matt Lowe Posted March 29, 2015 Share Posted March 29, 2015 attic is always fun Link to comment Share on other sites More sharing options...
Bullseye Posted March 29, 2015 Author Share Posted March 29, 2015 It's not bad, I have spray foam. But still I dont like it.What is strange is that with the other thermostat it works fine.I must be doing something wrong!!Thanks! Link to comment Share on other sites More sharing options...
Bullseye Posted March 12, 2016 Author Share Posted March 12, 2016 Reviving al old thread. I heard somewhere that it is a known problem an theres a patch to fix this issue (blowing heat instead of cold). Anybody heard about it?? Link to comment Share on other sites More sharing options...
mstafford388 Posted March 12, 2016 Share Posted March 12, 2016 I haven't heard of a patch for that. Doesn't mean there isn't one I don't know about though. sounds like you're not activating your reversing valve which would be the orange wire. Link to comment Share on other sites More sharing options...
Bullseye Posted March 13, 2016 Author Share Posted March 13, 2016 I am gona get a confirmation from my dealer monday or tuesday. I'll keep you posted!!! Link to comment Share on other sites More sharing options...
msgreenf Posted March 13, 2016 Share Posted March 13, 2016 The patch only applies in a very specific upgrade scenario. If you updated to 2.5 there was a problem with wrong firmware. Doesnt apply to any other upgrade path Sent from my Nexus 5X using Tapatalk Link to comment Share on other sites More sharing options...